We just moved into the new shop Monday, and we are having electrical issues.
What is happening, is some of the 120v outlets are dipping to 114v even with no load. This is enough to freak out our CMM controllers. Under 115v they shut down to protect themselves.
The building is 480v 600amp 3ph 4 wire, and we have a dry distribution transformer that is 45kVA 208Y/120v 3ph 4 wire. Breaker for transformer is 70 amps, and main breaker for 208/120 panel is 150 amp. Measured voltage at panels are:
480 = 492 (Edison checked this)
277 = 283
120 = 121.5
Most outlets are 120/121.
So I pop open the bizarre Cutler Hammer 208/120 breaker panel (took an hour to figure out how), and see some stuff that gets my Spider Sense tingling:
1) There are 32 single phase power leads, and 20 neutrals servicing them.
2) Some of the breakers have 2 or 3 wires screwed into their single terminal.
Item #1, I don't know if that's OK. Item #2, pretty sure that is NFG.
Sidebar: 1/2 of our 120v load is computers (switching power supplies, non-linear load). Is it necessary to change the transformer to a K-rated (K=4 or K=13) or is that overkill?
(McRat, not Kat)
What is happening, is some of the 120v outlets are dipping to 114v even with no load. This is enough to freak out our CMM controllers. Under 115v they shut down to protect themselves.
The building is 480v 600amp 3ph 4 wire, and we have a dry distribution transformer that is 45kVA 208Y/120v 3ph 4 wire. Breaker for transformer is 70 amps, and main breaker for 208/120 panel is 150 amp. Measured voltage at panels are:
480 = 492 (Edison checked this)
277 = 283
120 = 121.5
Most outlets are 120/121.
So I pop open the bizarre Cutler Hammer 208/120 breaker panel (took an hour to figure out how), and see some stuff that gets my Spider Sense tingling:
1) There are 32 single phase power leads, and 20 neutrals servicing them.
2) Some of the breakers have 2 or 3 wires screwed into their single terminal.
Item #1, I don't know if that's OK. Item #2, pretty sure that is NFG.
Sidebar: 1/2 of our 120v load is computers (switching power supplies, non-linear load). Is it necessary to change the transformer to a K-rated (K=4 or K=13) or is that overkill?
(McRat, not Kat)